Nie, dziękuję Przekieruj mnie tamAT PRO wrote:If you have much lower in the socket at the same time, you may have poor connections somewhere or too small a cross-section of wires.
ja_pizgam wrote:If the inverter raises the voltage so much, there is something wrong with it, it usually only raises 2-3V.
tomasz.ryszard wrote:You have high line impedance. Turn off the inverter and load this line with a 1kW heater. The voltage will probably drop by the same amount as the inverter picks up when it shuts down. If so, you have loose wires somewhere in the connector.When the inverter starts working, as the power increases, it raises the voltage from 236 V to 264 V and at exactly 1 kW it turns off.
gorajczanin wrote:I would like to change the country code to e.g. Germany to run on a higher voltage
gorajczanin wrote:I would like to change the country code to, for example, Germany to run on a higher voltage, but the code (password) 0001 does not enter in this case.
Rybus85 wrote:I wonder how the manufacturer could give so d..yi not to mount some cooling, only the heatsink itself. I keep the distances as if according to the instructions
Rybus85 wrote:I wonder how the manufacturer could give so d..yi not to mount some cooling, only the heatsink itself.
tomasz.ryszard wrote:Then swap the phases, connect it to another.The DSO electrician who changed the ordinary meter to a bidirectional one said something about the poor condition of a single-phase cable (I have a three-phase connection but a single-phase inverter).
Rybus85 wrote:And from a different barrel. What are the highest temperatures you've seen on the inverter? My record today ^^ 80 degrees. I wonder how the manufacturer could give so d..yi not to mount some cooling, only the heatsink itself. I keep the distances as if according to the instructions![]()
Wawrzyniec wrote:It's enough if you load this phase with turned off inverter. If there is a large voltage drop, the installation will be damaged. As the inverter will work, after loading this phase with a heater, you probably won't give anything to the grid anyway, because the inverter will work for the heater, and the interpretation with the inverter off is more obvious.
tomasz.ryszard wrote:On the other hand, the inverter, with the power of 1000 W generated on Sunday, boosted the voltage in the AC box of the inverter to 260-263 V from 237 V because this was more or less the voltage in the box when the inverter restarted (it did not generate power). This would correspond to a voltage drop of 23 - 26 volts.
tomasz.ryszard wrote:It seems that it is not too high line impedance that is causing too high voltage in the AC box, but inverter failure or something else.
wddd wrote:He said it's best to replace it with a new one when replacing because it often makes poor contact there "
Wawrzyniec wrote:It looks as if the inverter emits harmonics or the generated sine wave strongly differs in shape from the sine wave, and thus the voltage measurement by the inverter and the meter is falsified. And if the inverter detects too high voltage, it turns off. The voltage increase with the inverter operating at 1kW is certainly not greater than the voltage drop with the 1kW inverter switched on (with the inverter switched off). It may also be that this phase is very lightly loaded. If possible, connect the inverter to a different phase. This will rule out damage to the inverter, or choose other hours for measurements (higher network load)
tomasz.ryszard wrote:I am waiting for a sunny day so that the photovoltaic panels generate a power of at least 2 - 3 kW, then I will clearly load the working inverter in the ACE box with a 2000 W heater and possibly an additional 1200 W heater and see if it will continue to raise the voltage as high as in Sunday during the measurements.
tomasz.ryszard wrote:But in addition to the household load, there is an external (mains) load behind and before the medium voltage transformer. So I don't really understand why the inverter would not be loaded.
tomasz.ryszard wrote:If necessary, I will switch the inverter to another phase, although these other phases, as I wrote earlier, are unloaded (no sockets and lighting installations connected to these phases)
TL;DR: Field owners report 0–20 % daily energy loss when Sofar inverters trip on 253 V grid peaks; “set Country Code 12 for Poland and the problem goes away” [Elektroda, 3301, post #18624621] Why it matters: one menu setting often fixes most unexpected shutdowns without replacing hardware.
• Max. DC input voltage 1000 V & MPPT window 240-850 V (Sofar 8.8KTL-X manual [Uri, #18921613]) • Recommended DC/AC oversize ratio ≤ 1.2 : 1 for KTL-X models [Elektroda, BikeBarian, post #18360391] • Country Code list: PL = 12, DE = 07, NL = 05 [Elektroda, Defence & 3301, post #18851696] • Typical firmware: V2.30 (increases AC limit from 4.0 kW to 4.4 kW on 4.4KTL-X) [Elektroda, prose, post #19034268] • Service e-mail: service.pl@sofarsolar.com; hotline +48 22 123 98 58 [Elektroda, AT PRO, post #18772451]