TL;DR: Field owners report 0–20 % daily energy loss when Sofar inverters trip on 253 V grid peaks; “set Country Code 12 for Poland and the problem goes away” [Elektroda, 3301, post #18624621] Why it matters: one menu setting often fixes most unexpected shutdowns without replacing hardware.
Quick Facts
• Max. DC input voltage 1000 V & MPPT window 240-850 V (Sofar 8.8KTL-X manual [Uri, #18921613])
• Recommended DC/AC oversize ratio ≤ 1.2 : 1 for KTL-X models [Elektroda, BikeBarian, post #18360391]
• Country Code list: PL = 12, DE = 07, NL = 05 [Elektroda, Defence & 3301, #18851696]
• Typical firmware: V2.30 (increases AC limit from 4.0 kW to 4.4 kW on 4.4KTL-X) [Elektroda, prose, post #19034268]
• Service e-mail: service.pl@sofarsolar.com; hotline +48 22 123 98 58 [Elektroda, AT PRO, #18772451]
How reliable are Sofar inverters in everyday use?
Most 6–9 kW owners report trouble-free work for 1–3 years [Elektroda, iborkim, #18112697; Elekt...
Which menu code should I select for Polish grid parameters?
Use Country Code 12 (PL). It lifts the over-voltage trip to 253 V/10 min and 264 V/1 s, matching Polish NC-RFG limits [Elektroda, 3301, post #18851696] Selecting 07 (DE) raises the limit to 264 V but violates declaration of conformity.
My inverter shows ID01 ‘GridOFP’ and stops at noon—what now?
Measure L-N voltage; if it rises above 253 V, ask the DSO to lower tap settings or move PV to another phase. Until then, temporarily change Country Code to DE (07) or install a 230 → 220 V autotransformer [Elektroda, MariuszFEG, post #18623709]
What causes PvOVP / BusOPV errors on 4KTLM-G2 units?
Voc exceeds 600 V in cold sun. Split the 15-panel string into two of 8 + 7 or use a 3-phase inverter that accepts 1000 V DC [Elektroda, noja102, post #18323557]
How many Q-Cells 305 W modules can a Sofar 4KTLM-G2 safely handle?
Fourteen—seven per MPPT keeps each string below 2600 W and 600 V [Elektroda, kosmos99, post #18531958]
Is the MPPT Scan function worth enabling?
Enable only when partial shading occurs; it rescans the IV curve at user-set intervals. Service says it "improves harvest under shade" but reduces output 1–2 % on clean arrays [Elektroda, 3301, post #18622124]
How do I update Sofar firmware myself?
- Copy the /firmware folder to the SD card.
- Insert card, choose Menu → 5.Software Update, enter password 0715.
- Wait until ‘Update DSP1 OK’, ‘DSP2 OK’, ‘FUSE OK’, then reboot [Elektroda, Grucha383, post #19029218]
The display boots for one second at dawn—is that harmful?
No. The capacitors charge when DC rises above 180 V, then discharge if current is < 20 mA; this soft-start repeats without affecting lifespan [Elektroda, rydzyk673, post #19035241]
Why does Solarman show 0.9 A per phase even at 0 W?
Firmware ≤ V2.30 reports reactive standby current as active. Real clamp-meter reading is ~0.2 A; ignore the dash-board figure until a patch arrives [Elektroda, wilk125, post #19038447]
Edge case: can the inverter fail after a breaker trip?
Yes—one 8.8KTL-X died after a 16 A AC breaker opened; display stayed dark despite correct DC voltage, requiring warranty swap [Elektroda, gotycki1, post #18771167]
How to auto-run a 1.5 kW boiler only on surplus PV?
Install a PR-energised relay with the inverter’s CT loop; set closure above 4.5 kW export so the heater engages only in excess production [Elektroda, 3301, post #19053070]