Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar

Bob271 365148 1351
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #721 20015634
    szczukot
    Level 14  
    Well, not really - they just do their job. They are normal and therefore do nothing.
    Take the tension yourself first. What is the peak weather like at night.

    Fortunately, in great weather, it does not exceed 245V on any of the phases.
    The development of the FV is likely to happen now so I hope it can handle it somehow.
    And at night I have the order of 233V - which is a bit more than the average anyway.
    It seems to me that they care about more tension - then people use more and pay more :)
  • ADVERTISEMENT
  • #722 20015711
    xszuflax
    Level 11  
    szczukot wrote:

    Take the tension yourself first. What is the peak weather like at night.


    Hey, I know exactly what my tensions are:

    Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar

    Now 21:18, when there is no production anymore and I think there is still power consumption in the area, it looks like this:

    Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar

    The voltage on the vases is consistent +/- 1V. Tasmota is in a different phase than this measure.


    As for the power consumption of the neighbors, they pay the same for electricity from coal from Tauron as for mine. The difference is that Tauron is canceled for both sources, so IMO the more profitable it is to sell my local current by lowering the V on the transformer. They'll save on it from the net and maybe send it to some local factory.
  • #723 20016061
    szczukot
    Level 14  
    Exactly - this is how I thought that the "output" value was much over 230V :(
    And there is probably nothing to be done about it, because it is within the norm.
    I looked at my place - the output is also 237V. They conquer pretty well.
    however, I have a smaller number of PV installations. Some 60 houses are connected to the transformer. I don't want to count, but the installation is maybe 15-20.

    As for the fact that they will sell this electricity, it shouldn't be true. BO they assume that you are doing the installation as needed. So you will use as much as you produce (because you will buy some cheaper at night but ...)
    And at this point, dozens of houses next to you are paying more.

    Out of curiosity, you can see at the same time how much the meter and the inverter show. If there was a large turnout (that the inverter overstates), it may be a complaint that a poorly calibrated voltage sensor in the inverter causes continuous switching off. Although looking at the graph it will not work.

    I have one small idea, maybe it will work: write all letters that the voltage is still high and you are burning your appliances at home :) That someone's mixer is burnt, and someone's washing machine is on fire. And that during the repair they tell you that the voltage was too high. That you have some old devices for 220V etc. And just "Request to lower the voltage", because it never drops below 237V and is often under 253V.
    Maybe the "request" will work.
    When we switched from 220V to 230V, the standard said that it can only be up + 5% or + 6% - I don't remember. It is just to make the sherper devices come to life. And then it was raised to + 10% because it was assumed that the older devices are no longer available :)

    And the ecological method: buy a loft. The pigeons will blow the panels of the neighbors and the tension will drop ;)
  • ADVERTISEMENT
  • #724 20016076
    handsmick
    Level 2  
    Hello,

    Could anyone help me optimize my inverter settings it is a SUN2000-5KTL-L1

    First problem is not all short events are recorded for example if I use a kettle for a few minutes its not shown in the energy management graph so my energy consumption is not accurate.

    Second problem I have never produced the full 5kw that the inverter should supply I have only been able to generate 4.1kw with a 6kw demand despite bright sunshine at noon in May.

    I include some screen shots any help or suggestions would be great.
    Thanks
    Mick
    Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar
  • ADVERTISEMENT
  • #725 20016928
    szczukot
    Level 14  
    You have not even written what power panels you have installed.
  • #726 20017232
    zenq
    Level 12  
    xszuflax wrote:
    If the inverters trip at 253V, this standard will never be exceeded. The problem of inverter shutting down will never be solved either. Generally they have it in D.


    Change the inverter cutoff to 254-255V, then they will get their excess ;-)
  • #727 20017315
    Math13
    Level 14  
    I have a request.
    Suggest what amounts are entered as "Guaranteed tariff" and "Purchase price"?
    I think I configured it wrongly because I do not fully understand these two concepts.
    Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar
    Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar
  • ADVERTISEMENT
  • #728 20017502
    rokbok
    Level 38  
    I divided the gross amount on the invoice by the amount of kWh I used and I got a price of 1 kWh.

    The price we pay consists of so many derivatives
    that it is impossible to determine it exactly, therefore I took this and no other calculation.

    I entered the calculated amount in both positions in Fusion Solar, I take it with a grain of salt, as an approximate / approximate price for 1 kWh ;) .
  • #729 20020026
    guzi007
    Level 12  
    It was mentioned on the previous page about temperature, is there any info given at what temperature the power reduction begins?
    I have M1 installed in the garage, so far it is cool in the garage and Huawei is hitting 51 degrees.
  • #731 20020048
    lizak1983
    Level 15  
    Do you know to what extent this affects electricity production? In my summer, the temperature usually remains below 60 ° C during the highest production, but I found a day (July of the previous year) where it was 63 ° C. However, it is difficult to deduce anything from the graph, probably when the weather is nice and the day is hot, I will try to cool the inverter and see how the production will change, unless someone else does it before and shares the results of their observations.

    Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar
  • #733 20021120
    jmper
    Level 7  
    I haven't used the application to configure the inverter for a long time and now, when I logged in to FusionSolar, I saw this view:
    Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar
    There is nothing about any configuration of parameters here, to be honest there is almost nothing but a nice picture, if I click on the 3 dots at the top, I have there, among others. 'Settings' and only so much in them:
    Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar
    What to do how to live? I am using the latest version of FusionSolar for iOS, does it matter?
  • #734 20021202
    rokbok
    Level 38  
    After all, it says "Management System - Cannot Connect" at the top right.
    Without connecting to the inverter, you will not set anything, find the reason for the lack of communication.
  • #735 20021209
    jmper
    Level 7  
    rokbok wrote:
    It says "Management System - Cannot Connect" at the top right.
    Without connecting to the inverter, you will not set anything, find the reason for the lack of communication.

    If it were that simple, I wouldn't be writing here. This message was due to the problem that the dongle had with connection to Huawei's servers.
    Now everything is connected and I have exactly the same:
    Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar
  • #736 20021247
    rokbok
    Level 38  
    I wrote about what I noticed, maybe someone from iOS will say something more.
  • #737 20021279
    karol4000
    Level 12  
    jmper wrote:
    If it were that simple, I wouldn't be writing here. This message was due to the problem that the dongle had with connection to Huawei's servers.
    Now everything is connected and I have exactly the same:


    Are you logging in as an administrator?
  • #738 20021403
    jmper
    Level 7  
    karol4000 wrote:
    jmper wrote:
    If it were that simple, I wouldn't be writing here. This message was due to the problem that the dongle had with connection to Huawei's servers.
    Now everything is connected and I have exactly the same:


    Are you logging in as an administrator?


    Of course. Exactly as an installer. Interestingly, the installer password also works when logging in as a regular user. I don't know if it should be like that, but never mind. Unfortunately, the documentation of Huawei, to put it mildly, leaves much to be desired.
    I also wrote to the support, we'll see what they say.
  • #739 20021529
    handsmick
    Level 2  
    handsmick wrote:
    Hello,

    Could anyone help me optimize my inverter settings it is a SUN2000-5KTL-L1

    First problem is not all short events are recorded for example if I use a kettle for a few minutes it's not shown in the energy management graph so my energy consumption is not accurate.

    Second problem I have never produced the full 5kw that the inverter should supply I have only been able to generate 4.1kw with a 6kw demand despite bright sunshine at noon in May.

    Solar panels 12 Amerisolar 460W AS-6M-HC =5520 watts

    I include some screen shots any help or suggestions would be great.
    Thanks
    Mick
    Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar
  • #740 20021867
    Pitercom
    Level 14  
    Check if you have a strong WiFi signal because the inverter has a weaker sensitivity.
    If the signal is weak, it cannot connect.
  • #741 20022145
    jmper
    Level 7  
    Pitercom wrote:
    Check if you have a strong WiFi signal because the inverter has a weaker sensitivity.
    If the signal is weak, it cannot connect.

    Thanks, but that's not the problem at all. The signal will not be stronger because I am standing next to the inverter, the application on the phone connects to the inverter without any problem. Only then do the stairs begin, because earlier (as far as I remember) on the home page there were various configuration options to choose from, and now I have this charming picture with a house and current energy production and I can't see the possibility of setting / changing parameters anywhere for anything.
    I am beginning to have suspicions that they just threw out the configuration option from the iOS app, and I do not have an Android phone to check it. If someone could upload a screen from an android app, I would be grateful because I would know if it looks similar and where to enter the settings.
  • #742 20022225
    xszuflax
    Level 11  
    jmper wrote:

    I am beginning to have suspicions that they just threw out the configuration option from the iOS app, and I do not have an Android phone to check it.


    The iOS application works without any problems with new software, I tested from 140 - 142. Maybe you have too old firmware in the inverter and maybe the API has changed. Update the software via the website to 141 (142 not recommended).
  • #743 20022425
    rokbok
    Level 38  
    jmper wrote:
    If someone could upload a screen from an android app, I would be grateful because I would know if it looks similar and where to enter the settings.


    This is how it looks on andku, maybe try to clear the app's cache at home, or uninstall and reinstall it.

    Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar
  • #744 20022447
    sammyke007
    Level 1  
    Hi

    I have a SUN2000-4.6KTL-L1. It's working perfect, but I have one small problem.
    If I restart my router (weekly), the inverter loses internet connection and it won't reconnect for some hours. Is there a timeout setting that I can edit somewhere?
    Reading data thru the internal wifi AP is still working, but connection to my home wifi seems impossible after the router's reboot.

    Tnx
  • #745 20022722
    gmacko
    Level 15  
    Math13 wrote:
    Suggest what amounts are entered as "Guaranteed tariff" and "Purchase price"?


    I wrote it like this:
    I took only the variable fees into the unit price of kWh, because fixed fees would be independent whether I have PV or not.
    From what I received, I subtracted 20%, because what I produce for the warehouse, I can pick up less by 20% later, so in fact I will lose the 20% that I would "save" now.
    This app charges the same rate for auto consumption and exports, so it can't be otherwise.
  • #746 20022756
    Math13
    Level 14  
    gmacko wrote:
    Math13 wrote:
    Suggest what amounts are entered as "Guaranteed tariff" and "Purchase price"?


    I wrote it like this:
    ...

    This is a good patent. I type that too.
    Thanks.
  • #747 20022806
    gmacko
    Level 15  
    only calculate the gross kwh price in this way and for today, I have a VAT rate of 5%. It is not known what will happen next from June. Apparently, the shields and other sarahs are to be extended until the end of the year.
  • #748 20022812
    szczukot
    Level 14  
    And they say that from the new year electricity + 50%!
  • #749 20023711
    miikew1
    Level 6  
    for installation 9.69 and sun2000-8-m1, are the graphs below correct? cloudless sky, and it does not reach the maximum of 8.8, and on days with clouds it is from time to time it is 8.8 - is it the fault of the panel temperature?
    Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar Huawei SUN2000 Inverter: WIFI Dongle Connection, Firmware Update & FusionSolar
  • #750 20023731
    zenq
    Level 12  
    You have an 8kw inverter and are you surprised that it does not release 10?
    8kw inverter, will not output more than your 8.8 because that is how the limiter is set.
    For example, a 10kw inverter is factory set to a limit of 11kw.
    It is configurable in the app, but if you overdo it with max power, it will probably be limited by the temperature.

Topic summary

The discussion revolves around issues related to the Huawei SUN2000 inverter, specifically focusing on WiFi dongle connectivity, firmware updates, and the FusionSolar application. Users report difficulties in connecting the inverter to their home WiFi networks, with some resorting to using Ethernet cables for stable connections. Firmware updates are discussed, with users sharing experiences of updating both the inverter and the dongle, and the impact of these updates on inverter performance. The conversation also touches on the configuration settings for optimal production, including grid codes and reactive power compensation. Users express concerns about the limitations imposed by installers and the need for better access to their inverter settings.