kosmos99 wrote: Just note that the manufacturers recommend oversizing, so there can be no complaint or lack of professionalism.
Why do you write that the 8.8 model will not handle 10kW panels when the manual says that the maximum power of the panels is 12kW.
The manufacturer recommends (recommendation is not a requirement!) Oversizing because it is known that with 10kWp we will not get 10kW and the installation often does not have an optimal location (azimuth etc.) and hence the recommendations.
Practice shows that since 8.8kW cuts with well-lit 10kWp modules, it is not optimal, although the maximum efficiency is achieved for several days a year, mainly in spring.
12kW is the RECOMMENDED maximum power, with certainty due to the current-voltage protection. With poor elevation or azimuth NE and 20kWp, it will not be too high.
Oversizing might still make sense, if the difference between the inverters was not in the range of PLN 200-400.
Once the installer wanted + 2kPLN for the 2kW more power, then it made sense because
mostly the truncations are negligible.
If it cuts every day for a few hours, for me it is an assembly error (200 PLN / 2kW = 100 days of return).
Added after 40 [minutes]: slimax wrote: But in the case like today, when the whole day is sunny, the voltage does not reach the Pmax level, are the modules warmed up so much?
The panels lose their parameters with increasing temperature, e.g. -0.35% Pmax / ° C, where NOCT = 45 ? 2 ° C. When heated above 70 * C it can be even ~ 10% Pmax.
Therefore, if it cuts even in summer, it will "cut" in spring all the more.
For me, at 10kWp max in peak it was ~ 12.5kW (April 7),> 11kW happens often, while in continuous operation it rarely exceeds 10kW.
Now in summer it reaches 9.8kW, and on very hot days only slightly above 9kW (June 3).
The inverter 8.8 would cut this evenly almost daily.