. 1 string on 2 MPPT in parallel mode. The interesting thing is that I was looking for the original MC4 Staubli tees but nowhere to find only the stiff ones. I have the original MC4 for the entire installation and I did not want to have Chinese at the inverter, so I was forced to do it myself. I clamp all the ends and solder additionally.toolpusher wrote:Because I have a 6.5kWp installation on a 4.4 inverter. The currents and voltages are normal, but the power is a bit too high, although it does not matter, because whether it cuts from 6.5kW or 5.0kW is probably the same.
On the other hand, in this manual for installers, such connection is recommended - page 27 - Link
What may the loss of fitness be? Looking at the graph, for example, the 600 and 800V curve is practically horizontal from 50% of the power.
toolpusher wrote:Well, it seems to me that it has become cooler, but it is probably because 2 MPPT work but with less load. Besides, if it is the same inverter up to 6.6, I think it will be fine at 5.5.
theo33 wrote:toolpusher wrote:Because I have a 6.5kWp installation on a 4.4 inverter. The currents and voltages are normal, but the power is a bit too high, although it does not matter, because whether it cuts from 6.5kW or 5.0kW is probably the same.
On the other hand, in this manual for installers, such connection is recommended - page 27 - Link
What may the loss of fitness be? Looking at the graph, for example, the 600 and 800V curve is practically horizontal from 50% of the power.
The decrease in efficiency on weakly loaded inputs may be some, but probably negligible and if the graph relates to the AC output power, it is flat from 35%, but if it was also related to the power of the inputs, the load up to 3A at the input, i.e. up to 30%, would be losses. to be.
In my opinion, this parallel connection applies to strings connected in parallel when the summed current exceeds the capacity of the inverter input, while in your case it does not change anything, the previous limitation to 4.4 results from the output power after AC.
Once upon a time I made such attempts that I physically connected the inputs in parallel, but I left the settings independent and the current was distributed randomly, and in my opinion it was a result of the mppt algorithm because they will never work identically. And it looked like that with low powers one input worked, and with higher powers both. Unfortunately, I can't track these charts right now
Cytro12 wrote:The graph grows up to 50% and again decreases towards 100% load, I note that the given graph is for a high power inverter there is probably 12kW, the smaller the inverter, the lower the efficiency, but generally the characteristics match (similar components and algorithms). Fronius has a little different again for an example of a different solution. We take into account the point at which the inverter has been operating the longest, not the extreme conditions.
The independent work of MPPT here depends on the speed of the processor and the quality of the algorithm.
Cytro12 wrote:If Sofar has different algorithms for MPPT, this equipment is weak because they say that there are two independent MPPTs and it turns out that there is one and the other as a divisor because the inputs are too weak.
ZdzislawDyrmaZasadni wrote:Hello, I have a general attention to SOFAR inverters. According to in the current manual, these inverters must not be installed in basements or any other low-lying rooms, because min. the required distance from the ceiling must be 80 cm.
If someone has to buy Chinese, better choose SOLAX.
TL;DR: Field owners report 0–20 % daily energy loss when Sofar inverters trip on 253 V grid peaks; “set Country Code 12 for Poland and the problem goes away” [Elektroda, 3301, post #18624621] Why it matters: one menu setting often fixes most unexpected shutdowns without replacing hardware.
• Max. DC input voltage 1000 V & MPPT window 240-850 V (Sofar 8.8KTL-X manual [Uri, #18921613]) • Recommended DC/AC oversize ratio ≤ 1.2 : 1 for KTL-X models [Elektroda, BikeBarian, post #18360391] • Country Code list: PL = 12, DE = 07, NL = 05 [Elektroda, Defence & 3301, post #18851696] • Typical firmware: V2.30 (increases AC limit from 4.0 kW to 4.4 kW on 4.4KTL-X) [Elektroda, prose, post #19034268] • Service e-mail: service.pl@sofarsolar.com; hotline +48 22 123 98 58 [Elektroda, AT PRO, post #18772451]