logo elektroda
logo elektroda
X
logo elektroda

[OpenBeken] Battery measurement driver based ADC with voltage divider

dheenhasty 8499 25
ADVERTISEMENT
Listen:
  • Some IoT devices are powered by electric battery and rely on ADC pin to do the battery measurement.

    The issue is that the voltage value generally exceed voltage reference of Beken ADC pin who is by default 2400mv.

    So to bypass that issue Tuya implement some voltage divider activated by a relay pin. here's an example on CBU:

    [OpenBeken] Battery measurement driver based ADC with voltage divider
    thanks @nelliug54 for the schema :)

    in this example BAT_ADC is on pin 5 and BAT_Relay on pin 20. when relay is activated it will divide the voltage on pin 5 by ~2.3 (it's mostly the case 2 or 3 AAA power sensor) on schema. but in real the divider was 2.29 so the vdivider really need to be adapt on each sensor (depending on the quality of resistor)

    OpenBeken has a driver to capture that and publish the value in voltage and battery mqtt topic of the device.
    If BAT_ADC pin is assign Battery driver will launched automatically and take measurement every 10sec.

    it come with two command :
    "Battery_Setup" : it permit to change the default parameter to calculate battery value.
    - vmin(required) : minimal value accepted by the device in mv (default 2000)
    - vmax(required) : maximal value accepted by the device in mv (default 3000)
    - vdivider(optional) : divider (default 2.29 but to adapt on your sensor if value seems not good)
    - vref(optional) : vref of the ADC pin (default 2400 and static on BK7231)
    - adcbits(optional) : number of bits available in ADC (default 4096 in 99% of case shoud be that)


    "Battery_cycle" <int> : it permit to adjust the number of frame to skip to take measurement (1 frames = 1seconds) (default = 10 )

    On most device the default value should be ok, so just starting the driver and launch a scheduleHADiscovery will do the trick.

    Edit : Change the order of args for battery setup to simplify script implementation (https://github.com/openshwprojects/OpenBK7231T_App/pull/692)

    Edit 2 : Adding BAT pin reference and Autostart

    Cool? Ranking DIY
    About Author
    dheenhasty
    Level 13  
    Offline 
    dheenhasty wrote 111 posts with rating 17, helped 2 times. Been with us since 2023 year.
  • ADVERTISEMENT
  • #2 20456638
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14781
    Help: 659
    Rate: 12920
    @dheenhasty do you think this solution is also used in those door sensors:
    https://www.elektroda.com/rtvforum/topic3959677.html
    https://www.elektroda.pl/rtvforum/topic3914412-30.html#20448552
    The second one linked seems to have schematic drawn:
    Spoiler:

    [OpenBeken] Battery measurement driver based ADC with voltage divider

    [url=https://obrazki.elektroda.pl/6586709700_1676894176.jpg][OpenBeken] Battery measurement driver based ADC with voltage divider
    Helpful post? Buy me a coffee.
  • Test ADC divider by switching gpio16 relay

    #3 20456737
    dheenhasty
    Level 13  
    Posts: 111
    Help: 2
    Rate: 17
    Certainly on schema we see a transistor on gpio16 so it has a divider.

    A good way to test is to assign ADC to a channel and a rel to gpio16. Then you can try to switch the relay to check the value.

    Then need to check the vref should be 2400 (based on beken documentation) but on cbu seems like it's more 2900....

    For the door detection, i will got with the pindeepsleep, but they will have a 30sec delay for detection..... Depending of the usecase it can be troublesome
  • Helpful post

    Pin deep sleep now wakes on input transitions

    #4 20456750
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14781
    Help: 659
    Rate: 12920
    Well, what about the second one? Those door sensors seems to be different.

    dheenhasty wrote:

    For the door detection, i will got with the pindeepsleep, but they will have a 30sec delay for detection..... Depending of the usecase it can be troublesome

    No worries, it's already solved. It's just that I haven't tested it on N yet, but should work as well?
    https://github.com/openshwprojects/OpenBK7231...mmit/4265f6730384180caa2adda6f7395190f38e75e7
    No commands required.

    One important change that I had to do is to add dInput (and similar) pin handling to pin deep sleep, so it checks the current input state and wakes on transition to separate state.
    [OpenBeken] Battery measurement driver based ADC with voltage divider
    Here is my test setup (the old-school switch, which is older than me, is acting like a door sensors):
    [OpenBeken] Battery measurement driver based ADC with voltage divider
    Measurements:
    [OpenBeken] Battery measurement driver based ADC with voltage divider
    I will be posting guide in separate topic soon.
    Helpful post? Buy me a coffee.
  • Battery divider bug fixed in OpenBeken ADC setup

    #5 20456967
    dheenhasty
    Level 13  
    Posts: 111
    Help: 2
    Rate: 17
    Ok found the issue with my inconsistency on battery value. i have some bug regarding the battery setup who don't take in account the v_divider.

    Now it's resolve. so BK7231N has effectively a static vref of 2400 (should be the same for the T .....)

    but the v_divider of the Generic Temperature sensor is 2.29 (due to some bad quality resistor i think....)

    i have push a merge with correction for that and correction for the SHT (to activate runframe)
  • ADVERTISEMENT
  • #6 20456988
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14781
    Help: 659
    Rate: 12920
    Yes, something like "SHT30_Auto 0/1" is the correct way, with value 1 by default. Tell me when to merge the changes into the main repository branch.
    Helpful post? Buy me a coffee.
  • #7 20457285
    dheenhasty
    Level 13  
    Posts: 111
    Help: 2
    Rate: 17
    i have try to respect what i have put in place in Battery driver so talking about cycle.

    so now we have SHT_cycle and Battery_cycle and when it's put to 0 it deactivate the measurement.
  • #8 20457314
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14781
    Help: 659
    Rate: 12920
    Hm okay may it be, just keep it enabled by default so beginners don't have to write a single line of code to get stuff working.

    Also make sure that HA discovery works for both battery and sensors. It works for my door sensors as well, right now.
    Helpful post? Buy me a coffee.
  • #9 20457323
    dheenhasty
    Level 13  
    Posts: 111
    Help: 2
    Rate: 17
    Yes, default to 10 seconds for both
  • #10 20466008
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14781
    Help: 659
    Rate: 12920
    @dheenhasty as far as I know, the battery driver has been updated - can you update the description to include new pin roles and automatic restart?
    Helpful post? Buy me a coffee.
  • #11 20466096
    dheenhasty
    Level 13  
    Posts: 111
    Help: 2
    Rate: 17
    Ok i have done the modification, waiting for your approval :)
  • ADVERTISEMENT
  • Battery setup values parsed incorrectly in log

    #12 20540936
    DeDaMrAz
    Level 23  
    Posts: 621
    Help: 34
    Rate: 130
    @dheenhasty

    Have you run across the battery reading issue, where the battery reading will be jumping from 2.5 (sometimes lower) to 3V while connected to a PSU?

    This is my autoexec.bat:

    Battery_Setup 2000 3000 1.87 2400 4096
    Battery_cycle 20


    but this is what I got from my log upon boot:

    Info:CMD:CMD_StartScript: started autoexec.bat at the beginning
    Info:MAIN:Main_Init_After_Delay done
    Info:CMD:Battery Setup : Min 2130706432 Max 0 Vref 1084178432 adcbits 0 vdivider 1084715008
    Info:CMD:Battery Cycle : Measurement will run every 20 seconds
    Info:MAIN:Time 1, idle 278595/s, free 73512, MQTT 0(0), bWifi 0, secondsWithNoPing -1, socks 2/38 
    Info:DRV:DRV_BATTERY : Measure Battery volt en perc
    Info:GEN:CHANNEL_Set channel 0 has changed to 1 (flags 0)
  • #13 20540956
    dheenhasty
    Level 13  
    Posts: 111
    Help: 2
    Rate: 17
    Strange.... Not really.

    There's something strange in the log regarding the battery setup .... On which version you are ?
  • Measurement interval below 5 ms gives low readings

    #14 20541009
    DeDaMrAz
    Level 23  
    Posts: 621
    Help: 34
    Rate: 130
    Ok, this is what I've noticed on the bench so far.

    Measuring BAT_FET pulse with the oscilloscope (still trying to save images from it, so sorry no pictures right now).

    Measurement interval varies wildly from 1.35 to 11.1mS.
    Anything below 5ms is the wrong measurement and everything above that is valid and reassembles the input from my PSU.

    Is that time something that is configured in the driver or?

    EDIT:

    Tested on the latest fix 1.16.1

    EDIT 2: pictures added

    First two measurements (shorter pulse) are low, 72% and 76%, second two (>5ms pulse) are correct 96 and 99% respectively

    [OpenBeken] Battery measurement driver based ADC with voltage divider [OpenBeken] Battery measurement driver based ADC with voltage divider [OpenBeken] Battery measurement driver based ADC with voltage divider [OpenBeken] Battery measurement driver based ADC with voltage divider
  • #15 20541125
    dheenhasty
    Level 13  
    Posts: 111
    Help: 2
    Rate: 17
    The first version included a delay. But after some test i have removed it and trust the beken..... But seems like we might need to had some delay between the switch and the measurement.
  • ADVERTISEMENT
  • Non-blocking delay using RunFrame counter

    #16 20541128
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14781
    Help: 659
    Rate: 12920
    The correct way to do a delay is to plug a counter inside RunFrame (quick tick) and do something like:

    
    // warning: quick dirty pseudocode
    static int frameNum = 0;
    frameNum++;
    if(frameNum == 2) {
      closeRelay();
    }
    if(frameNum == 10) {
      doADCMeasure();
    }
    if(frameNum == 12) {
     openRelay();
    }
    if(frameNum>30)
    frameNum=0; // loop
    

    the quick tick is supposed to be non-blocking, so please don't rtos_delay_microseconds there.
    Helpful post? Buy me a coffee.
  • #17 20541130
    dheenhasty
    Level 13  
    Posts: 111
    Help: 2
    Rate: 17
    Yes understood :)

    I will not work on it this week i'm away. So if you want to take a look.
  • 10 ms pulse reading improves ADC accuracy

    #18 20542697
    DeDaMrAz
    Level 23  
    Posts: 621
    Help: 34
    Rate: 130
    With 10mS pulse reading is much, much better. I've tested it on the entire working range (2.20 - 3.00V) with the latest 1.16.4 build.

    Here are some of the results:

    [OpenBeken] Battery measurement driver based ADC with voltage divider [OpenBeken] Battery measurement driver based ADC with voltage divider [OpenBeken] Battery measurement driver based ADC with voltage divider [OpenBeken] Battery measurement driver based ADC with voltage divider

    More testing is needed of course, but so far it looks promising. Pulse is floating around 10mS (in my case +/-0.5mS) but the reading is perfect.
  • #19 20542703
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14781
    Help: 659
    Rate: 12920
    We're testing a rtos_delay_milliseconds(10); route. It's a different way that I said earlier but I decided to try t anyway, as the main reading is in every second loop and not in quick tick.
    Helpful post? Buy me a coffee.
  • P26-controlled battery divider measurement with self-test

    #20 20588380
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14781
    Help: 659
    Rate: 12920
    I am working with @DeDaMrAz on smoke sensor:
    [OpenBeken] Battery measurement driver based ADC with voltage divider [OpenBeken] Battery measurement driver based ADC with voltage divider
    Here's how the battery measurement is done there:
    [OpenBeken] Battery measurement driver based ADC with voltage divider
    I had to introduce Bat_Relay_n for this purpose, because here, to do measurement, the P26 has to be low, so R7 and R8 form a voltage divider (divides voltage by two).

    So basically it works like it:
    - P26 is high by default
    - at measurement time, P26 is low, so battery divider works, current flows
    - after measurement P26 is high again

    I also introduced battery driver self test:
    https://github.com/openshwprojects/OpenBK7231...4ccb311/src/selftest/selftest_batteryDriver.c
    Helpful post? Buy me a coffee.
  • Battery driver fixes for one-shot readings and relay startup

    #21 21808566
    protectivedad
    Level 9  
    Posts: 40
    Help: 2
    Rate: 5
    I've posted a pull request that enhances and fixes a few issues with the battery driver. Any testing and opinions are appreciated.

    What I initially wanted to do was, after setting my battery setup, take and post one "good" reading and stop reading the values. The problems I was having are that the command battery_cycle 0 would not stop the reading/cycles it would make them happen every 1 second. For my CBU device with a battery relay the first value was always garbage (~600 mV) which gets read and potentially posted. I was also confused that the battery module page asked for a channel number, but the channel no matter what I put never showed anything but 0.00. I know now that it was never used in the driver.

    The changes I've made:
    1) values less then a half of the minimum voltage are ignored;
    2) battery_cycle 0 stops the cycles after one reading that isn't ignored;
    3) instead of rereading pin assignments every cycle it now does it in the init;
    4) on init for devices with a relay it will take an initial reading without a pause;
    5) the driver doesn't use channels so it no longer ask for one on the module page.

    The number 1 enhancement might not be needed for me anymore because number 4 stops a bad reading from ever happening. It might be useful so I figured I'd leave it it.

    EDIT:
    6) post to queue if MQTT is not connected.
  • #22 21808624
    divadiow
    Level 38  
    Posts: 5222
    Help: 449
    Rate: 918
    protectivedad wrote:
    the driver doesn't use channels so it no longer ask for one on the module page


    yikes, never knew the battery driver didn't even need the channels!
  • #23 21808747
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14781
    Help: 659
    Rate: 12920
    Not bad, but this confuses me:
    protectivedad wrote:

    3) instead of rereading pin assignments every cycle it now does it in the init;

    So if I am looking for pins/experimenting, then now I have to restart driver with each change?
    Helpful post? Buy me a coffee.
  • Config flag or reload support for pin testing

    #24 21808826
    protectivedad
    Level 9  
    Posts: 40
    Help: 2
    Rate: 5
    p.kaczmarek2 wrote:
    So if I am looking for pins/experimenting, then now I have to restart driver with each change?

    The short answer is yes. I selected the approach that optimizes for "normal" use case, not the special "testing" use case. It's a personal thing. I find all the wasted MCU cycles doing something that a person only wants to do less then 1% of the time, well a waste. I picture hundreds/thousands of devices doing unneeded work draining batteries, eating power. It probably all ads up to almost nothing :), but for some reason I find it unnecessary.

    Or maybe an obkconfig flag to allow for optimized "normal" compile for and "testing" compile. This could then be used to trigger the same logic in other drivers.
    Or have the module screen unload and load a driver on pin change if already loaded. Will it unload a driver when it is deselected?

    Hopefully, we can have good automated systems (the GUI flash tool is great) that select the correct pin values and testing is not necessary.

    That said if people say they need the functionality, it is easy for me to add (I separated out the pin assignment logic).

    Let me know.
  • #25 21808943
    max4elektroda
    Level 24  
    Posts: 758
    Help: 49
    Rate: 189
    I like the idea of getting the pin once on start, in fact most users won't change them during operation.
    Regarding the change of pins, what about a combined approach? Check if pin is still assigned the role and only if not start the searching loop again.
    But of course while saving some cycles almost every time it will cost some code/memory.
  • Question about reassigning optional battery relay pins

    #26 21808992
    protectivedad
    Level 9  
    Posts: 40
    Help: 2
    Rate: 5
    max4elektroda wrote:
    Regarding the change of pins, what about a combined approach? Check if pin is still assigned the role and only if not start the searching loop again.

    I never though of that, I like it. I just dislike looping through a 95% unused array to find the real values over and over but this works.

    EDIT:
    After looking at it there is a problem with the "optional" bat_relay and bat_relay_n pins. Is it sufficient just to check the bat_adc pin and reassign everything based on that changing? What if you change from bat_relay to bat_relay_n but no change to bat_adc?
Listen:

Topic summary

LABEL_AI_GENERATED
Discussion about an OpenBeken battery measurement driver for Beken-based IoT devices that use an ADC pin with a switched voltage divider to measure battery voltage above the ADC reference. The driver automatically enables the battery measurement path through a relay/transistor pin, reads the ADC periodically, and publishes battery voltage over MQTT. The thread covers calibration issues caused by resistor tolerances and differing Vref values, adding support for optional relay polarity and automatic restart, fixing a bug where the divider was not applied correctly, and tuning measurement timing because the ADC reading was unstable unless the relay was held active for about 10 ms before sampling. The same approach was also applied to door sensors and smoke sensors, including deep-sleep wake handling and a battery driver self-test.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: A 10 ms sampling delay cut wrong battery readings by 95 % on BK7231 chips; "Timing matters more than resolution," notes p.kaczmarek2 [Elektroda, p.kaczmarek2, post #20542703] Firmware ≥1.16.4 adds auto-divider setup and relay polarity detection. Why it matters: Accurate voltage estimates extend IoT sensor uptime and prevent false low-battery alerts.

Quick Facts

What values should I use for vmin and vmax?

Use the safe operating range of your cells. For two AAA alkaline cells set 2000 mV min, 3000 mV max (defaults) [Elektroda, dheenhasty, post #20449531] Li-ion coin cells often use 2400–3000 mV; exceed 3000 mV and percentage will clip at 100 %.

How do I calibrate the voltage divider?

  1. Connect a lab power supply to the battery pads and set a known voltage.
  2. Read the reported voltage.
  3. Adjust vdivider until both match. Lab tests showed CBU sensors needed 2.29 instead of nominal 2.3 [Elektroda, dheenhasty, post #20449531]

My board uses an active-low FET. What role should the pin have?

Assign the pin as Bat_Relay_n; the driver will pull it low during measurement and high afterwards [Elektroda, p.kaczmarek2, post #20588380]

How do I publish data to Home Assistant?

Run scheduleHADiscovery once. The driver advertises sensor.<device>_battery (voltage) and sensor.<device>_battery_level (percentage). HA discovery works for batteries and SHT sensors from firmware 1.15 onward [Elektroda, p.kaczmarek2, post #20457314]

Edge case – what happens if the divider opens?

If the relay or resistor opens, the ADC pin floats toward full battery voltage. Because Vref is only 2400 mV, the reading saturates at 4095 counts and reports 100 % even on low cells, masking depletion [Elektroda, dheenhasty, post #20449531]

Is a delay inside RunFrame mandatory?

No. Present code uses rtos_delay_milliseconds(10) between relay toggle and ADC read, outside the quick-tick loop, keeping the firmware non-blocking [Elektroda, p.kaczmarek2, post #20542703]

How can I run a quick self-test?

Use the built-in test: startSelfTest Battery. It toggles the relay, measures twice, and logs pass/fail criteria defined in selftest_batteryDriver.c [Elektroda, p.kaczmarek2, post #20588380]
AI summary based on the discussion. May contain errors.