SOFAR 8kW PV Installation: Opinions, Durability, Failures & Experiences with Inverters
---Ryba--- 512298 1722
How reliable are Sofar inverters for an around-8 kW PV installation, and what problems or failures do users report?
Users report mostly acceptable results: one 6.6KTL-X had no problems for over a year, and another 8.8KTL-X owner said a firmware update to v2.20 removed the old clipping around 8 kW and let the inverter reach full peak power [#18112697] [#18662870] [#19158337] The most common problems in the thread were not outright inverter defects but installation/configuration mistakes: too many panels in one string or the wrong input mode caused DC overvoltage errors such as PvOVP, BusOPV or permanent fault, and the cure was to wire the strings correctly and keep each MPPT within its limits [#18322870] [#18323108] [#18359020] [#18360610] [#18699492] Another recurring issue was grid overvoltage: users saw ID01/Grid OVP shutdowns when mains voltage rose to about 253 V, and one case reached 280 V at the customer side; the inverter was behaving as designed in those cases [#18624602] [#18665849] A few users also mentioned Wi‑Fi/software quirks and awkward warranty handling, with the installer, seller, distributor and Sofar service bouncing responsibility between each other [#18306997] [#18322870] [#18323064] [#18331261] [#18772451] There was at least one real hardware failure report, where an 8.8KTL-X tripped AC overcurrent after about a month and then would not restart, so the unit had to go through warranty [#18771167]
  • #181 18760813
    matmatimateusz
    I am going to install the installation and I am hesitating about two proposed solutions:
    First option:
    PV RISEN ENERGY RSM 60-6 310M MONO SILVER MODULE - 12 pcs
    INVERTER SOFAR 3.3KTL-X Three-phase
    Second option:
    PV RISEN ENERGY RSM MODULE 120-6- 330M MONO HALF CUT BLACK - 13pcs
    SOFAR INVERTER 4,4KTL-X Three-phase
    The prices of these installations (the valuation for me) differ cosmetically.
    My 2019 electricity consumption is 3100kwh, but I expect it to increase.
    (I am installing a 5kW air conditioning, the family will grow in some time etc.)
    at the same time, I don't want to know how much to build in reserve.
    The roof is almost perfectly south, not shaded (even with a chimney), so I'm not going to install optimizers.
    I expect you to pick the second option, but I'm curious about your opinions about these kits.
    PS.
    I'm not going to change the models of panels or the inverter anymore :)
  • #182 18760831
    kosmos99
    Help: 338
    Rate: 820
    In the first, the permissible generator power (3600W) will be exceeded
    Option two, then.
  • #183 18760842
    matmatimateusz
    I know, but apparently some exceedances are allowed.
    I'm not an electrician so it's hard for me to argue with that.
    The full power installation works rather rarely (which is understandable), and even if it exceeds the maximum value,
    at most the inverter will cut off. Please correct me if I am wrong.
    of course, with the second instance, I still have the option of adding, for example, 2 panels in the future.
  • #184 18760854
    kosmos99
    Help: 338
    Rate: 820
    3600 is already an excess, because the rated power of the inverter is 3000W.
    The first option will not meet your current consumption in full, you will have to buy about 500kWh.
  • #185 18760869
    matmatimateusz
    Ok, that's two more questions.
    The question of optimizers - south roof, 25st, no shading - I understand that in this case it is an unnecessary cost?
    RISEN ENERGY RSM 120-6- 330M MONO HALF CUT BLACK panel - any opinions?
    If not about the panel, then about the producer in general?
    (I will only mention that I have a nice price for them, which undoubtedly "improves" them :) )
  • #186 18763197
    AT PRO
    Help: 63
    Rate: 191
    I will not write you which option will only give food for thought regarding panels - inverter.
    I have one 3.6 kW installation in Jinko solar plus sofar 3.3 Ktl-x panels and the second still unfinished (half of the panels) 5.58 kW the cheapest panels Just solar (310w) plus 10 kW Fronius and on average the second has twice the yield at a given time than on the other the one with the sofa.
    Sofar solar is a nice inverter and works fine, but it looks like there is a difference to Fronius.
    Oh, and on the second installation, the panels are flatter, maybe that has such a big impact? The same direction.
  • #187 18763339
    kosmos99
    Help: 338
    Rate: 820
    The rated power of this Sofar is 3kW (max 3.3), which is 600W of panel power you lose. In addition, Sofar is loaded to the maximum, so its temperature is probably higher, so the losses are greater.
    It would be more reliable to compare inverters of the same power with the same panels.
  • #188 18763628
    AT PRO
    Help: 63
    Rate: 191
    The fact that a loss is a consent because you can see on the chart how it cuts with equal sunshine.
    The temperature of the inverters is not higher because I have both of them in the open air on the ground. Fronius often does not even start the fan and the sofar does not exceed 50 degrees. Now if I put it together, Sofara would give it 4.4.
    Fronius of the 5.58 produced the most 6.9 kW.
    When I have time, I plan to connect these 3.6 to Fronius and see what they show then, I just have to invest in 40 m of cables.
  • #189 18766820
    Grucha383
    Rate: 19
    Someone tried to send data from sofara to server other than Chinese? There's a Remote Server B setting on the datalogger, but I don't know how to figure it out
  • #190 18767885
    AT PRO
    Help: 63
    Rate: 191
    Someone wrote about it somewhere but I don't remember which thread. I have accounts on solarmanpv.com and home.solarman.cn and I only send to both that I only entered the datalogger number in both.
    Which server would you like to send to?
  • #191 18768411
    zbig205
    Rate: 56
    Hello. What do you think about the Sofar 3.6KTLM-G2 + 11 pcs. RISEN SOLAR 330W. What to suggest when choosing panels?
  • #192 18769203
    AT PRO
    Help: 63
    Rate: 191
    The price and amount of space available for their assembly.
    I have Jinko Solar 400W, half mono perc etc. etc. and the advantage is short cables that do not hang under them, besides, no revelation in relation to the cheapest mono Just solar 310W. Even I have the impression that the cheap ones are sorted more to the customer's advantage, i.e. when the test gave 315W or more, they did not throw it immediately to 315W or 320W.
  • #193 18769421
    Cytro12
    Help: 47
    Rate: 304
    To match the inverter and our temperatures.
  • #194 18770532
    zbig205
    Rate: 56
    So how do you rate this statement?
  • #195 18771167
    gotycki1
    Rate: 8
    Hello. I have a problem with the sofarsolar 8.8ktl-x inverter. Yesterday the overcurrent protection on the AC side worked, it is not known why and the inverter itself turned off and cannot be started. On the DC and AC side everything is ok but the inverter is dead. Do you know what is the cause? The inverter worked for 1 month, it is under warranty, but I do not know if it is and how their service in Poland works. Let me know if you know anything.
  • #196 18771230
    theo33
    Help: 78
    Rate: 322
    From the DC itself, the display should light up, if nothing else, check the voltage on the mc-4 plugs, the dc circuits, if you have through fuse-links, then to be checked, and the overcurrent one is what amperage and does it still throw it?
  • #197 18771290
    gotycki1
    Rate: 8
    The DC voltage is ok. I checked the inserts - they are conductive. 16A AC overcurrent does not eject when armed.
  • #198 18771526
    Leon444
    Help: 48
    Rate: 355
    What to look for, the inverter burnt if it threw the protection, that is, there was a short circuit in the device. You are guaranteed to use it.
  • #199 18771666
    gotycki1
    Rate: 8
    I think so too, I just wonder how with the service in Poland. How long may it take to repair.
  • #200 18771745
    theo33
    Help: 78
    Rate: 322
    Warranty with invoice via distributor or retailer,
    Dc voltage what? how many modules connected to the input?
  • #201 18771794
    gotycki1
    Rate: 8
    560V input, 16 modules per string.
  • #202 18771814
    theo33
    Help: 78
    Rate: 322
    It's ok. It's below 1000, I wanted to make sure that maybe the voltage didn't exceed
    I wonder if this damage was influenced by any external conditions, were there any discharges nearby? and did the 25A pre-meter protection also work?
  • #203 18772376
    gotycki1
    Rate: 8
    At the time of the failure, there was no storm or lightning. There was a storm that day, but a few hours earlier. The 25A pre-meter protection also worked.
  • #204 18772413
    slaslo
    Help: 24
    Rate: 56
    Kolego gotycki1 as soon as the complaint procedure starts, describe who took care of it and how it is going.
    I think that every Sofar owner will be interesting.
  • #205 18772451
    AT PRO
    Help: 63
    Rate: 191
    SOFARSOLAR Poland
    ul. Jórskiego 30, 03-584 Warsaw
    VAT: PL5272915147 | REGON: 385117650 | KRS: 0000819731
    T: +48 22 4902099
    E: service.pl(_at_)sofarsolar.com
    SERVICE
    T: +48 22 123 98 58
    E: serwis(_at_)sofarsolarpoland.pl
    www.sofarsolarpoland.pl
    Poland Distributor and Service partner
    Corab Sp. z o. o
    EnergyNAT Sp. z o. o
  • #206 18772522
    gotycki1
    Rate: 8
    Thank you very much for sending the contact to the website.
  • #207 18772655
    kris161rp030
    Hello, I bought a Sofar 11KTL-X for my PV installation last week. Are the certificates from this file sufficient to report to the energy company https://fotowoltaika.corab.eu/do-pobrania/c certaty/c certaty-falownik-sofar - do you still have to look for or attack the seller? Greetings
  • #208 18772712
    Cytro12
    Help: 47
    Rate: 304
    Yes, it should be enough, I also attached the manufacturer's certificates with the application.
  • #209 18772771
    gotycki1
    Rate: 8
    I attached the certificate I just downloaded from the Corab website and it was accepted.
  • #210 18816831
    zbig205
    Rate: 56
    Gentlemen, an urgent matter. Do you know something about the SUNGROW company, namely the SUNGROW SG3K6-D model.
    I was supposed to have a Sofar Solar 3.6KTLM-G2 installed and SUNGROW has just arrived. Should you request replacement according to the contract or agree to this inverter?
Discussion about Sofar PV inverters for an ~8 kW installation focuses on reliability, long-term experience, and common faults. Several users report generally stable operation of Sofar units such as 6.6KTL-X and 5.5KTL-X, but also mention issues with Wi‑Fi connectivity, missing service support, and occasional inverter shutdowns under certain weather conditions. The main technical problem analyzed is DC input overvoltage: a 1-phase Sofar inverter with a 600 V maximum input was connected to a string of 15 Q.CELLS 305 W modules, causing PvOVP / BusOPV errors and shutdowns when string voltage exceeded the limit, especially in cold, sunny conditions. The proposed fix was to split the array into two strings and connect them to separate MPPT inputs, or redesign the inverter choice and string sizing. The thread also covers MPPT limits, string voltage calculations, current limits, Sunspec/RS485 compatibility, Polish menu/software availability, and comparisons with SMA and Fronius as higher-priced alternatives.
TL;DR: Field owners report 0–20 % daily energy loss when Sofar inverters trip on 253 V grid peaks; “set Country Code 12 for Poland and the problem goes away” [Elektroda, 3301, post #18624621] Why it matters: one menu setting often fixes most unexpected shutdowns without replacing hardware.
• Max. DC input voltage 1000 V & MPPT window 240-850 V (Sofar 8.8KTL-X manual [Uri, #18921613]) • Recommended DC/AC oversize ratio ≤ 1.2 : 1 for KTL-X models [Elektroda, BikeBarian, post #18360391] • Country Code list: PL = 12, DE = 07, NL = 05 [Elektroda, Defence & 3301, post #18851696] • Typical firmware: V2.30 (increases AC limit from 4.0 kW to 4.4 kW on 4.4KTL-X) [Elektroda, prose, post #19034268] • Service e-mail: service.pl@sofarsolar.com; hotline +48 22 123 98 58 [Elektroda, AT PRO, post #18772451]
How reliable are Sofar inverters in everyday use?
Most 6–9 kW owners report trouble-free work for 1–3 years [Elektroda, iborkim, #18112697; Elekt...
Which menu code should I select for Polish grid parameters?
Use Country Code 12 (PL). It lifts the over-voltage trip to 253 V/10 min and 264 V/1 s, matching Polish NC-RFG limits [Elektroda, 3301, post #18851696] Selecting 07 (DE) raises the limit to 264 V but violates declaration of conformity.
My inverter shows ID01 ‘GridOFP’ and stops at noon—what now?
Measure L-N voltage; if it rises above 253 V, ask the DSO to lower tap settings or move PV to another phase. Until then, temporarily change Country Code to DE (07) or install a 230 → 220 V autotransformer [Elektroda, MariuszFEG, post #18623709]
What causes PvOVP / BusOPV errors on 4KTLM-G2 units?
Voc exceeds 600 V in cold sun. Split the 15-panel string into two of 8 + 7 or use a 3-phase inverter that accepts 1000 V DC [Elektroda, noja102, post #18323557]
Is the MPPT Scan function worth enabling?
Enable only when partial shading occurs; it rescans the IV curve at user-set intervals. Service says it "improves harvest under shade" but reduces output 1–2 % on clean arrays [Elektroda, 3301, post #18622124]
How do I update Sofar firmware myself?
  1. Copy the /firmware folder to the SD card.
  2. Insert card, choose Menu → 5.Software Update, enter password 0715.
  3. Wait until ‘Update DSP1 OK’, ‘DSP2 OK’, ‘FUSE OK’, then reboot [Elektroda, Grucha383, post #19029218]
The display boots for one second at dawn—is that harmful?
No. The capacitors charge when DC rises above 180 V, then discharge if current is < 20 mA; this soft-start repeats without affecting lifespan [Elektroda, rydzyk673, post #19035241]
Why does Solarman show 0.9 A per phase even at 0 W?
Firmware ≤ V2.30 reports reactive standby current as active. Real clamp-meter reading is ~0.2 A; ignore the dash-board figure until a patch arrives [Elektroda, wilk125, post #19038447]
Edge case: can the inverter fail after a breaker trip?
Yes—one 8.8KTL-X died after a 16 A AC breaker opened; display stayed dark despite correct DC voltage, requiring warranty swap [Elektroda, gotycki1, post #18771167]
How to auto-run a 1.5 kW boiler only on surplus PV?
Install a PR-energised relay with the inverter’s CT loop; set closure above 4.5 kW export so the heater engages only in excess production [Elektroda, 3301, post #19053070]