  • Teardown and OBK flashing of the Tomzn TOMPD-63 WIFI smart circuit breaker, distinguished from the TOMPD-63LW model that also cuts neutral.
  • Inside, it uses two PCBs: a latching relay board with BL0942 metering and power supply, plus an LCD/Tuya MCU/WB3S board.
  • Tuya DpID extraction identified 13 IDs, including total forward energy, switch, leakage current, breaker id, and over-voltage protect/recovery timers.
  • OBK flashed through RX, TX, and GND without cutting traces, then autoexec.bat started the TuyaMCU driver, mapped channels, and enabled MQTT/Home Assistant discovery.
  • Some UI fields remain unclear, including the extra "t" setting, and "Alarm set 2" does not display well.
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Listen:
  • 5–10 second updates are enough for ICP warning use case

    #91 20956764
    morgan_flint
    Level 14  
    Posts: 251
    Help: 4
    Rate: 63
    Angel0fDeath wrote:
    Is it really necessary to know the state of dpID 6 each second or half second?

    Not as fast, 5 or even 10 seconds, like this device does, is enough. But 5 minutes, as the other device has, seems too much even for "simple" applications, don't you think?

    Angel0fDeath wrote:
    Probably if you share your idea, why you need such high refreshments we can think something...

    Well, one of my ideas is to implement a device that warns when something called "ICP" is going to trip, also indicating how long it will take to trip. "ICP" stands for "Interruptor de control de potencia" (Power control breaker) and is something implemented in Spanish's smart meters to avoid customers taking more power than they are paying for. But it's not a simple power or current limit, but it has a rather generous inverse time curve so it will trip faster the further you go over the limit. For example, it will allow you to drain 150% of your contracted power during 15 minutes, but if you go to 200% it'll trip in less than 5 min. So I'd like to have some kind of warning (sound, traffic light or the like) that allows to react and turn off something before the meter trips (and somebody start crying because he lost all his work in his computer...). I tink 5-10 seconds update time is enough for this application. I have 9 kW in my contract but have an instant electric water heater of 24 kW (it never reaches full power in normal conditions). Usually, I don't have problems during a shower (let's say 3-5 min), but if I have one or two HVAC units connected at the same time, I probably would have a blackout. A further improvement would be to turn off the air conditioning when power reaches a certain amount, taking into account the inverse time curve or not.

    Angel0fDeath wrote:
    And if you really need such quick update you can probably consider buying some professional devices... But speaking about professional devices - the only difference probably will be the price and reaction time of the protections. Well reliability also. You will always receive the info with delay... it is always 'post factum' - after event occurs

    You're right, but I don't really need that (and less want to pay the price!). Another possibility I'm considering is simply using PZEM-004T module(s) (I have three phase at home) directly connected to an ESP module (already did some experiments with them). Or, maybe, something like this connected to the ESP module via MODBUS (I think OBK doesn't implement it). Of course, the poor documentation doesn't state refresh rate but, if it's like with the PZEM, you send a command and get a response quite fast (I tested them with 1 second and even less).

    p.kaczmarek2 wrote:
    So, as far as I know, it's not possible to request single DP update. That's a shame, they could very well just allow sending 0x08 command with a single payload byte as argument (dpID) and report only that, but as far as I know, there is nothing like that in Tuya specs
    I agree, shouldn't have been very difficult for them to implement it like that, but we'll have to live with it ☹️
  • ADVERTISEMENT
  • 10-second updates are accurate enough for 63A load

    #92 20957477
    Angel0fDeath
    Level 13  
    Posts: 118
    Help: 2
    Rate: 33
    @morgan_flint Yep 5-10 sec. update time will be enough. If your heater is operating at full power (24kWh) this will be about 6.7 Ws. Updating each 10 sec will give about 67W difference which according to me is enough accuracy. Of course you can update each 5 sec. also. Even if you have 36 kW connected to the device it is still about 100 W difference for 10 sec. But I think your heater is 3 phases, so you need other device.
    For this device - 220V * 63A = 13.86 kW (max), which is about 3.85Ws - update each 10 sec is enough. And this in case you use full power.... There will be no big difference if you make calculation with 240V...
  • #93 20957555
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14770
    Help: 659
    Rate: 12913
    A very cool addition to a device page would be a graph chart. It would have to be, of course, fully clientside, and it would most likely forget the data once you close the page (and it would store the data only as long as the page is open), but it still could be done relatively easily with all the freely available javascript chart libraries that are around here.
    Helpful post? Buy me a coffee.
  • 10-second updates are accurate enough for power monitoring

    #94 20957624
    morgan_flint
    Level 14  
    Posts: 251
    Help: 4
    Rate: 63
    Angel0fDeath wrote:
    @morgan_flint Yep 5-10 sec. update time will be enough. If your heater is operating at full power (24kWh) this will be about 6.7 Ws. Updating each 10 sec will give about 67W difference which according to me is enough accuracy. Of course you can update each 5 sec. also. Even if you have 36 kW connected to the device it is still about 100 W difference for 10 sec. But I think your heater is 3 phases, so you need other device.
    For this device - 220V * 63A = 13.86 kW (max), which is about 3.85Ws - update each 10 sec is enough. And this in case you use full power.... There will be no big difference if you make calculation with 240V...

    You are talking about using DpID1 (energy) for this application, but it's also possible to use DpID 6 (power).

    For a three-phase system, I'd need something like the three-phase counter I linked in my previous post or, alternatively, three single-phase devices... better without the switch, to avoid unbalance in case of spurious tripping of one or two of them.
  • ADVERTISEMENT
  • Device page should stay for setup and live monitoring

    #95 20957665
    Angel0fDeath
    Level 13  
    Posts: 118
    Help: 2
    Rate: 33
    Yes, using dpID1 doesn't require very often updates, since changes are not so rapid. Using dpID6, since these are moment values, require more often updates. But you can always take actions at some safety level - for instance if you have moment power over 10kW (or 2 kW, if your heater is on) do something. In this case again 10 sec update should be enough.
    You can even limit the breaker by max. current for some period (while your heater is on) and after that to remove limitation. In this case you even not need to know what happens... The device will automatically strip the line if max. current exceeded.

    Added after 8 [hours] 46 [minutes]:

    Quote:
    A very cool addition to a device page would be a graph chart.

    @p.kaczmarek2 In general - yes could be done. It is very easy to log the values in memory. However I probably cannot understand the practical reason for this. I can combine all data in lets say 2 graphs, but first you should wait a lot of time to see something on this graphs with incomming data only, and second this will involve loading of some packages from internet (if you dont have them on your pc) - something which I would like to avoid. And third the current idea is you can host this page in device. Im not sure it will be possible to host all graph libraries in the device, although we recently solved such issue.
    The main purpose of this page (according to me) is everybody to be able to set the device with desired settings, since firmware currently cannot do it and after that just to monitor the moment values from home automation server where you can issue whatever graphs you want. The intention of this page is not to replace home automation server. Development of this page also shows some alternative ways (work around) to set everything from home automation server. I almost have finished this integration in perl for FHEM. Hassio is written in python and in general can do this also, but Im pretty sure here we have more hassio entusiast which can do this better than me.
    You can even set the device from browser or linux command prompt (curl). My script shows how. The way somebody will do it - depends on the choice.
    So for now - no graphs. Will finish reworking of the script for the other device. Then will add detail comments. Then you will have the honor to merge them in your Github repository. And then I can focus on other projects, which btw includes my LIST and RTOS delay.
    All of us here lost a lot of time working on this device. It is time to say over - now we have all instruments to do whatever we want with the device. Of course if driver includes all these features we dont need alternative control page.
    Yes... I know you are alone and this device has only 2M flash... Will try to help as much as I can, but this remainds me something - have you ever considered modular building - for this device we need only tuyamcu driver, ok some device from the same type probably will need ntp driver as well. Why we need the rest 29 drivers in this device? Everybody likes full builds, but when you have only 2M flash probably this should be reconsidered. I have ir blaster with CB2S chip. On this device I use only ir driver. I dont need the rest 30 drivers. Instead of them I preffer larger IR library... But the last comment is another story and probably another topic... Sorry
  • ADVERTISEMENT
  • Compile-time options to trim firmware for 2M flash

    #96 20973837
    jkwim
    Level 13  
    Posts: 186
    Help: 4
    Rate: 25
    Angel0fDeath wrote:

    Yes... I know you are alone and this device has only 2M flash... Will try to help as much as I can, but this remainds me something - have you ever considered modular building - for this device we need only tuyamcu driver, ok some device from the same type probably will need ntp driver as well. Why we need the rest 29 drivers in this device? Everybody likes full builds, but when you have only 2M flash probably this should be reconsidered. I have ir blaster with CB2S chip. On this device I use only ir driver. I dont need the rest 30 drivers. Instead of them I preffer larger IR library... But the last comment is another story and probably another topic... Sorry


    Could a TASMOTA style compile time options be a solution to build only the required libraries?
  • Compile-time driver flags already exist in obk_config.h

    #97 20974514
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14770
    Help: 659
    Rate: 12913
    @jkwim but there already is a TASMOTA style compile time options system:
    https://github.com/openshwprojects/OpenBK7231T_App/blob/main/src/obk_config.h
    Code: C / C++
    Log in, to see the code

    It's just that all public builds are done with the same config.

    @Angel0fDeath how's the progress on the page?
    Helpful post? Buy me a coffee.
  • ADVERTISEMENT
  • #99 20975909
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14770
    Help: 659
    Rate: 12913
    You are missing ".h". This link works for me:
    Screenshot of a GitHub repository displaying the obk_config.h file of the OpenBK7231T_App project.
    Helpful post? Buy me a coffee.
  • No further development needed for TOMPD-63 WIFI

    #100 20988207
    Angel0fDeath
    Level 13  
    Posts: 118
    Help: 2
    Rate: 33
    Quote:
    @Angel0fDeath how's the progress on the page?


    @p.kaczmarek2 The page for TOMPD-63-LW just posted in corresponding topic :)

    https://www.elektroda.com/rtvforum/topic3995777-60.html#20988137

    For this device there will be no further development since everything is working fine.
    Big delay, but was really busy with other errands... Remains only to add comments and to submit both pages on GH repository :) . Will try to do this tomorrow. For TOMPD-63-LW page must wait @morgan_flint to confirm everything is ok, since I don't have such device
  • #101 20988424
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14770
    Help: 659
    Rate: 12913
    I think a separate topic in Smart Home Tutorials with basic info how to setup it and and how it looks like (screenshots) would be also very useful. Good job.
    Helpful post? Buy me a coffee.
  • Script now derives device name from filename

    #102 20988474
    Angel0fDeath
    Level 13  
    Posts: 118
    Help: 2
    Rate: 33
    @p.kaczmarek2 Ok. Will do it... and will try to do it tomorrow :)

    Added after 1 [hours] 50 [minutes]:

    @morgan_flint Last change in html file. The only change is I changed the name of the file according to device name. Now the script will take device name and revision number from the filename. It seems now we have a lot of devices which more or less can use this script, so it is mandatory to make a difference between devices... I made corresponding changes in the script for TOMPD-63-LW and EAMPDW-TY63 also. The latter scripts published in corresponding topics :)
    Attachments:
    • TOMPD-63-WIFI_rev7.zip (5.6 KB) You must be logged in to download this attachment.
  • Request for review of added HTML comments

    #103 20988918
    Angel0fDeath
    Level 13  
    Posts: 118
    Help: 2
    Rate: 33
    @p.kaczmarek2 @morgan_flint I added comments to last rev7 of html. I would like to ask you, if possible, to review the comments and if something not clear to notify me. According to me everything is clear, but let's not forget I wrote the code, so for me everything is clear...

    So, please review it. If necessary will add more comments and after that - ready to publish it in GH and Tutorial Page.
    Thank you in advance.
    Attachments:
    • TOMPD-63-WIFI_rev7 - with comments.zip (6.4 KB) You must be logged in to download this attachment.
  • Blank baseURL for LittleFS and new send function

    #104 20989473
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14770
    Help: 659
    Rate: 12913
    This segment:
    
    			let baseURL = "http://192.168.0.220";
    		    //let baseURL = "";
    

    could be commented to say that (as I understand it) you can have URL blank when used on LittleFS and enter URL if you are testing on PC.

    The rest looks good, however, it could be slightly improved with the new send function that allows for arbitrary payloads and packet types but still calculates the checksum:
    https://github.com/openshwprojects/OpenBK7231...mmit/7a9d3df40d4c20cee56ed9bfe4d9927ce44c20c1
    Helpful post? Buy me a coffee.
  • Autoexec.bat submitted as GitHub PR

    #105 20989795
    Angel0fDeath
    Level 13  
    Posts: 118
    Help: 2
    Rate: 33
    Quote:
    I think a separate topic in Smart Home Tutorials with basic info how to setup it and and how it looks like (screenshots) would be also very useful. Good job.


    @p.kaczmarek2 Done. You can find it here:

    https://www.elektroda.com/rtvforum/topic4040354.html

    Added after 2 [hours] 40 [minutes]:

    @p.kaczmarek2 Autoexec.bat for this device submitted on GH repository as PR. The folder is docs/autoexecs.

    https://github.com/openshwprojects/OpenBK7231T_App/pull/1110

    Can't find in which folder to make PR for html file. There is a folder docs/scripts but I find only .bat files there... Can you advise, please?
  • Update autoexec JSON source and separate docs dir

    #106 20990046
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14770
    Help: 659
    Rate: 12913
    You are supposed to update the JSON source:
    https://github.com/openshwprojects/OpenBK7231T_App/blob/main/docs/json/autoexecExamples.json
    Then the MD files will be built when I run node scripts/getcommands.js in the repository.

    Added after 46 [seconds]:

    PS: and autoexec sample should be in separate dir, not in the "docs", but here:
    https://github.com/openshwprojects/OpenBK7231T_App/tree/main/docs/autoexecs
    Helpful post? Buy me a coffee.
  • #107 20990058
    Angel0fDeath
    Level 13  
    Posts: 118
    Help: 2
    Rate: 33
    autoexec is exactly there, or at least I created it there. For html script - will check now. Thank you.

    Hmm... The link with json's you've sent - it looks like it treats only different autoexec.bat files....
    Please either write more detailed instructions on how to proceed or just include the attached files....
    Attachments:
    • TOMPD-63-WIFI_rev7.zip (6.46 KB) You must be logged in to download this attachment.
    • TOMPD-63-WIFI.zip (1.47 KB) You must be logged in to download this attachment.
  • #108 20990066
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14770
    Help: 659
    Rate: 12913
    The linked PR adds autoexec.bat to the docs directory itself, and not to the "autoexecs" dir:
    Screenshot from GitHub showing a merge request for the autoexec.bat file for the TOMPD-63-WIFI project.
    Helpful post? Buy me a coffee.
  • #109 20990074
    Angel0fDeath
    Level 13  
    Posts: 118
    Help: 2
    Rate: 33
    @p.kaczmarek2 Ok. Sorry for that. First time making PR on your site.... Please just add both files I have sent in previous post where necessary. Thank you.
  • Docs and script credit added to BK7231N teardown

    #110 20990090
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14770
    Help: 659
    Rate: 12913
    Sure, let me add that for you.
    Here's first commit:
    https://github.com/openshwprojects/OpenBK7231...mmit/99c9d2a009c347a574e24a1be17802fe7da5a34d
    And now here is docs build:
    https://github.com/openshwprojects/OpenBK7231...mmit/7e59270362367a95e41796f069c6e1ef3436b0d9
    I think it looks good! Can I also add something like "script by Angel0fDeath"? Your work deserves a credit.
    Snippet of REST script code for TuyaMCU with annotations.
    Helpful post? Buy me a coffee.
  • Missing HTML file in autoexec additions

    #111 20990132
    Angel0fDeath
    Level 13  
    Posts: 118
    Help: 2
    Rate: 33
    @p.kaczmarek2 First - thank you. On your question - you can add whatever you want or you think is appropriate.
    However, I think there is something wrong with addition - you added autoexec.bat but html file still not added (according to the links above.

    EDIT: After check of GH repository again - autoexec is added to docs/autoexecs and to docs/autoexecExamples - 2 commits which is correct. I cannot find where html file is added...
  • Where to add the HTML control page

    #112 20990137
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14770
    Help: 659
    Rate: 12913
    Angel0fDeath wrote:

    However, I think there is something wrong with addition - you added autoexec.bat but html file still not added (according to the links above)

    We don't have currently a place for HTML files in that doc repo, that's why it's linked to your article there:
    Alternative control html page for TOMPD-63-WIFI
    I am not sure how to handle that, where would you suggest adding HTML?

    Or maybe I should add that to this repo:
    https://github.com/openshwprojects/OpenBekenRESTDemo/tree/main
    Helpful post? Buy me a coffee.
  • #113 20990140
    Angel0fDeath
    Level 13  
    Posts: 118
    Help: 2
    Rate: 33
    I think docs/html or docs/htmlExamples will be clear enough.
    EDIT: Or something like that... In general you can organise this folder as autoexxecs, but the name will be html. Currently I don't thing you need json for this folder... but who knows... After few weeks probably 2 more html files will be submitted - for the other similar devices, so up to you
  • #114 20990144
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14770
    Help: 659
    Rate: 12913
    hm but that would make this repository obsolete:
    https://github.com/openshwprojects/OpenBekenRESTDemo/tree/main
    wouldn't it?
    Helpful post? Buy me a coffee.
  • #115 20990151
    Angel0fDeath
    Level 13  
    Posts: 118
    Help: 2
    Rate: 33
    Yep. Agree.
    But in general what we post - these files this is not a demo - they are working files with the correct device. So I don't think it is correct to call them demo.
    From the other point of view - everything could be called DEMO....
  • Successful BK7231N flash on TOMPD-63-WIFI breakers

    #116 21309399
    leśny_ziutek
    Level 12  
    Posts: 52
    Help: 3
    Rate: 9
    I'd like to report that I successfully flashed two TOMPD-63-WIFI smart breakers using the below command:

    uartprogram OpenBK7231N_QIO_1.17.769.bin  -d /dev/ttyACM0 -w --unprotect -s 0x0


    Both my breakers has the CB3S module instead of WB3S. They also have the backlight mounted under the display but it's disabled (the part with the LED connection to the board is filed down).

    The autoexec.bat from the https://www.elektroda.com/rtvforum/topic4040354.html thread works OK. But I have a trouble coping the TOMPD-63-WIFI_rev7.html:

    Error:LFS:No more free space 12
    Error:API:Failed to write to TOMPD-63-WIFI_rev7.html with error -28


    Will try to remove all comments from both files and try again but in the current form this file set seems to be too big.

    I've also a problem with the drag-and-drop way to sending files to the device on Linux. Can an alternate way (select a file from disk) be added do the WebApp?
  • Hosting alternative HTML page in LittleFS after trimming comments

    #117 21309469
    morgan_flint
    Level 14  
    Posts: 251
    Help: 4
    Rate: 63
    leśny_ziutek wrote:
    Will try to remove all comments from both files and try again but in the current form this file set seems to be too big.

    From this post and in the new thread opened to continue the discussion about hosting the web app on the device, you can find some considerations about LittleFS size, how to increase it, and how to adapt the block size to make better use of it.

    Following the advice there, I was able to host the alternative control HTML page in the device, adapted to GR2PWS, even including an special 7-segment font:
    LittleFS file management interface with HTML code editor. User interface of the OpenBK7231N system control panel with various data and settings.

    I also removed all the comments from the HTML to save some space. The only problem I've had is the one mentioned here by @p.kaczmarek2 , related to OTA overwriting LittleFS space, but it was solved simply clearing all files and restoring them from a backup
  • #118 21310404
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14770
    Help: 659
    Rate: 12913
    leśny_ziutek wrote:
    . Can an alternate way (select a file from disk) be added do the WebApp?

    Sure, added:
    Screenshot of a user interface with the Upload file button circled on a file management options page.
    Helpful post? Buy me a coffee.
  • LiteFS upload button simplifies flashing on Linux and Android

    #119 21310442
    leśny_ziutek
    Level 12  
    Posts: 52
    Help: 3
    Rate: 9
    After removing all comments, empty lines and indentation from both files they fit into standard LiteFS. The file sizes are as below:

    /TOMPD-63-WIFI_rev7.html - 20316
    /autoexec.bat - 1733

    And I found the "Upload file" button that makes my life easier on Linux and also enables using Android phone/tablet to upload files (I couldn't find a way to drag-and-drop anything on Android). Is this button a new feature or somehow I didn't notice it before?

    Dodano po 3 [minuty]:

    p.kaczmarek2 wrote:
    Sure, added:


    I thought I hadn't noticed it! Thanks!
  • Hosting the control HTML in LittleFS with a 7-segment font

    #120 21315367
    jkwim
    Level 13  
    Posts: 186
    Help: 4
    Rate: 25
    morgan_flint wrote:
    leśny_ziutek wrote:
    Will try to remove all comments from both files and try again but in the current form this file set seems to be too big.

    From this post and in the new thread opened to continue the discussion about hosting the web app on the device, you can find some considerations about LittleFS size, how to increase it, and how to adapt the block size to make better use of it.

    Following the advice there, I was able to host the alternative control HTML page in the device, adapted to GR2PWS, even including an special 7-segment font:
    LittleFS file management interface with HTML code editor. User interface of the OpenBK7231N system control panel with various data and settings.

    I also removed all the comments from the HTML to save some space. The only problem I've had is the one mentioned here by @p.kaczmarek2 , related to OTA overwriting LittleFS space, but it was solved simply clearing all files and restoring them from a backup


    Neat!
Listen:

Topic summary

LABEL_AI_GENERATED
Discussion about teardown, TuyaMCU reverse engineering, and OpenBeken flashing of the Tomzn TOMPD-63 WIFI smart breaker based on BK7231N/CB3S hardware. The thread compares it with similar devices such as TOMPD-63LW and EAMPDW-TY63, identifies DpIDs and their meanings, and works through several firmware issues: raw/string payload parsing, setup values for leakage and overcurrent/overvoltage thresholds, fault reporting, breaker ID, and prepaid energy handling. A custom OpenBeken alternative control HTML page was developed to read and set DpIDs directly, including raw hex-string access via MQTT/HTTP, plus support for flags, channel mapping, and LittleFS hosting. The discussion also confirms the hidden LCD backlight/light-source setting by wiring an LED to unused pads, and notes that the same scripts and parsing approach can be adapted to the related TOMPD-63-LW device.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: This FAQ helps OpenBeken users flash the Tomzn TOMPD-63 WIFI and map its 13 DpIDs correctly. "Everything seems to be ok" once DpID raw access is enabled, but DpIDs 17, 18, and 19 need special handling, and DpID 12 clears both energy counters on this model. [#20925322]

Why it matters: The TOMPD-63 WIFI looks similar to other Tuya breakers, but its hardware, relay behavior, raw DpIDs, and counter logic differ enough that a copied configuration can fail.

Model Relay switching Key DpID differences Energy clear behavior
TOMPD-63 WIFI Cuts line only DpIDs 1, 6, 9, 11–19, 104, 105 DpID 12 clears total and prepaid energy
TOMPD-63LW Cuts line and neutral Adds DpIDs 21 and 101; different 104/105 meaning Counters can be cleared separately

Key insight: Treat the TOMPD-63 WIFI as its own platform, not a TOMPD-63LW clone. The breakthrough was OBK raw DpID access over HTTP/MQTT, which exposed DpIDs 17, 18, and 19 as usable hex or string data instead of broken integers. [#20931165]

Quick Facts

  • The TOMPD-63 WIFI teardown identified 13 DpIDs: 1, 6, 9, 11–19, 104, and 105, before OBK flashing began. [#20869137]
  • The protection action time in DpID 104 is documented as 1–30 s, but device users reported menu control in 0.5 s steps from 0.5 s to 30 s. [#20879436]
  • The recovery delay can be set from 1 to 500 seconds, and the action time and recovery time affect real protection behavior after faults and restarts. [#21508925]
  • One user bought the device for 11.56€, with a more typical price around 19€, which explains why it became a popular hacking target despite firmware quirks. [#20883189]
  • Newer hardware revisions appeared with CB3S, CBU, and header-accessible modules; one late board revision no longer required soldering because RX, TX, VCC, and GND were reachable through headers. [#21453780]

How do I flash a Tomzn TOMPD-63 WIFI with a BK7231N/WB3S or CB3S module using OpenBeken, and which RX, TX, VCC, and GND connections are needed?

You can flash it over UART by wiring RX, TX, VCC, and GND to the Wi-Fi module pads or header. 1. Disconnect the small display/Wi-Fi board from the power board. 2. Solder only RX and TX if VCC and GND are already on the header. 3. Power VCC only when the flasher starts, because that avoids interference from the Tuya MCU. Early WB3S boards needed two wires plus header power; later revisions exposed all pins on headers, and CB3S units also flashed successfully with uartprogram ... -w --unprotect -s 0x0. [#21453780]

What is the difference between the TOMPD-63 WIFI and the TOMPD-63LW, especially in relay switching, DpIDs, and energy counter behavior?

The TOMPD-63 WIFI cuts only the line, while the TOMPD-63LW cuts both line and neutral. Up to DpID 19, most DpIDs match, but the LW adds DpID 21 for leakage test and DpID 101 for clearing the main energy counter, and its DpIDs 104 and 105 mean power factor and frequency instead of protection timing. The biggest user-visible difference is DpID 12: on the WIFI model it clears both prepaid and total energy, while on the LW it clears only prepaid energy. [#20921587]

How can I extract and identify the Tuya DpIDs for the TOMPD-63 WIFI before replacing the stock firmware with OBK?

Extract the DpIDs from Tuya first, then flash OBK after you know the map. 1. Use the Tuya developer workflow described in the linked tutorial to pull the product JSON. 2. Read the abilityId, code, and typeSpec fields for each property. 3. Build your OBK autoexec.bat from those DpIDs. The TOMPD-63 WIFI exposed 13 DpIDs, including phase_a on DpID 6, fault on DpID 9, switch on DpID 16, and timing controls on DpIDs 104 and 105. [#20869137]

Why does DpID 104 on the TOMPD-63 WIFI show only integer values in OBK or tuya-mqtt.js when the device menu allows 0.5 second steps?

It shows integers because the Tuya MCU reports DpID 104 as an integer value even when the device UI offers 0.5 s steps. Users verified that setting 0.5 s on the breaker appears as 0 in OBK, while 1.0 s and 1.5 s both transmit the same integer payload. The thread conclusion was that the limitation comes from the Tuya MCU firmware or protocol handling, not from the front-end page. That makes 0.5 s steps visible on the device itself but not reliably readable through OBK or tuya-mqtt.js. [#20880051]

What does the mysterious 't' setting on the Tomzn TOMPD-63 WIFI actually control, and how was the LCD backlight pad identified?

The t setting controls the LCD backlight timeout. A user reopened the device, found two unused pads on the small PCB, and traced one to ground and the other through a resistor and transistor that looked like an LED driver. After soldering an LED to those pads and setting t to a low value, the LED turned on after a button press and switched off after the programmed time. The manual called it a “light source,” and the hardware test confirmed it was a prepared backlight function. [#20883603]

How should I configure autoexec.bat for the TOMPD-63 WIFI so DpID 6, 9, 17, 18, 19, 104, and 105 work correctly in OpenBeken?

Use TuyaMCU, enable Wi-Fi-paired behavior, and map raw or string DpIDs carefully. DpID 6 should use RAW_TAC2121C_VCP; DpID 9 should be mapped as raw for full fault bitmaps; DpIDs 17 and 18 should be kept as raw or handled via raw send commands; DpID 19 should be mapped as str; and DpIDs 104 and 105 should be mapped as val. Start with clearIO, SetFlag 46 1, startDriver TuyaMCU, tuyaMcu_setBaudRate 9600, and tuyaMcu_sendQueryState. That arrangement was the stable end-state after several revisions. [#20954679]

Why do raw TuyaMCU DpIDs like 17, 18, and 19 fail to parse correctly as integers or strings in some OBK builds, and what workaround was added?

They fail because those DpIDs are longer raw or string payloads, not simple 32-bit values. DpID 17 is 4 bytes and can sometimes fit, but DpID 18 is 12 bytes and overflows integer-style parsing, while DpID 19 is a string like ETU9-IOT-WIFI. The workaround was to add raw DpID access so OBK could expose raw payloads as hex strings and strings directly over HTTP and MQTT instead of forcing broken integer conversion. That feature landed through the Dp and DPxx commands with a flag-controlled implementation. [#20924258]

How can I read raw TuyaMCU data as hex over HTTP or MQTT using the OBK Dp and DPxx commands?

Enable the raw DpID feature, map the DpIDs, then query them with Dp or DPxx. Dp returns a JSON array of all mapped DpIDs, including id, type, and data, while DP23 returns one DpID only. Over HTTP, users called IP/cm?cmnd=Dp; over MQTT, the same command published JSON to the stat topic. Raw fields appear as hex strings, and string DpIDs like 19 appear as decoded text. This solved the long-standing visibility problem for DpIDs 17, 18, and 19. [#20925335]

What is RAW_TAC2121C_VCP in OpenBeken, and how does it map the phase_a packet into voltage, current, and power channels?

“RAW_TAC2121C_VCP” is a packet parser that decodes Tuya’s phase_a raw meter frame, splitting one 8-byte payload into voltage, current, and active power channels. It exists because DpID 6 is not a plain number; it is a packed VCP measurement block. In newer OBK usage, you should provide the first channel index after RAW_TAC2121C_VCP, and OBK will place voltage first, current next, and power last in VCP order. If the channel order is wrong, readings or relay behavior can break. [#21363688]

What is a DpID in the Tuya ecosystem, and why does it matter when migrating a smart breaker from Tuya firmware to OpenBeken?

“DpID” is a Tuya data-point identifier that links one device function to a defined payload type, access mode, and meaning, such as a relay state, fault bitmap, energy counter, or raw measurement packet. It matters because OBK must map each DpID correctly to a channel or parser. If you guess wrong, the breaker can show bad values, miss alarms, or reject writes. On this device, DpID 6 carries raw VCP data, DpID 9 is a fault bitmap, and DpIDs 17–19 need special raw or string handling. [#20869137]

Why does the TOMPD-63 WIFI clear both total energy and prepaid energy with DpID 12, while the TOMPD-63LW clears them separately?

The TOMPD-63 WIFI simply implements DpID 12 differently from the TOMPD-63LW. Users tested it and confirmed that triggering DpID 12 on the WIFI model resets both DpID 13 prepaid energy and DpID 1 total energy. On the LW model, separate DpIDs exist for separate clears, so the logic is cleaner. The mistaken “Clear Prepayment” label in early OBK examples came from copying the LW setup, then it was corrected to “Clear Energy Counters” after testing. [#20881929]

What is the best way to decode the TOMPD-63 WIFI fault bitmap from DpID 9 into readable alarms in Home Assistant, FHEM, or a custom web page?

The most reliable method is to treat DpID 9 as raw data and decode the bitmap in software. The thread showed a simple loop that checks each bit against a 17-item label array, then builds readable text such as Overvoltage, Overcurrent, or Leakage Current. Users also found that single-byte and two-byte fault payloads confused integer parsing, while raw handling fixed it. In practice, a custom page or server-side script is better than forcing OBK text channels, especially when multiple alarms are active at once. [#20883083]

How do I host the alternative TOMPD-63-WIFI HTML control page on LittleFS when the file is too large, and what can I trim or reconfigure to make it fit?

Trim the HTML and autoexec.bat, or increase usable LittleFS space. Users made the page fit standard LittleFS by removing comments, blank lines, and indentation, reducing the HTML to 20,316 bytes and autoexec.bat to 1,733 bytes. Another option is to reconfigure LittleFS size and block settings, then restore files after OTA if needed. A newer WebApp also added an “Upload file” button, which helped Linux and Android users upload the trimmed files without drag-and-drop issues. [#21310442]

Why does the relay toggle misbehave when using certain channel orders with RAW_TAC2121C_VCP, and how should VCP channels be assigned in newer OBK builds?

The misbehavior comes from newer RAW_TAC2121C_VCP parsing rules. Once you specify the starting channel index, OBK expects VCP order: voltage first, current second, power third. One user saw the relay toggle switch off after one second when DpID 16 and VCP channels were arranged badly, but the issue disappeared after moving the VCP block earlier and respecting its channel order. Later fixes restored backward compatibility for the old no-index style, but the safer method in new builds is explicit VCP ordering. [#21367632]

How can I make an Atroch GR2PWS or similar Tuya-based power relay stay off at power-up until voltage conditions are safe, instead of energizing the relay for several seconds first?

You may not be able to do that with the stock startup behavior. A later user reported that the Atroch GR2PWS energizes its relay for about 10 seconds after power-up, then starts measuring and enforcing rules, which creates a risk window if mains voltage is already unsafe. The thread did not provide a confirmed OBK-side fix for forcing an always-off boot state on that model. For safety-critical use, treat that startup pulse as a known limitation until a model-specific workaround is tested and verified. [#21624931]